High pressure cutout switch not working?

Tested the jeep today after getting tired of not having AC. The low side is fine but the high side is hitting over 300psi. What do the high pressure cutout switches stop them at? When you manually cycle the compressor it blows cold. Any insight? Overfilled? Low?
Reply With Quote
  #2  
Old June 20th, 2009, 16:30
chpmnsws6 chpmnsws6 is offline
NAXJA Forum User
 
Join Date: Jan 2009
Location: Springfield IL
Posts: 819
Re: High pressure cutout switch not working?

http://www.bestvalueautoparts.com/it...ON S&weight=1

If the high pressure switch is needed, is this it? How do you test the switches?
Reply With Quote
  #3  
Old June 20th, 2009, 16:39
Saudade's Avatar
Saudade Saudade is offline
NAXJA Member
 
Join Date: May 2005
Location: SoCal
Posts: 2,427
Re: High pressure cutout switch not working?

"The high pressure cut-off switch contacts are open when the discharge line pressure rises above 3100 to 3375 kPa (450 to 490 psi). The switch contacts will close when the discharge line pressure drops to 1860 to 2275 kPa (270 to 330 psi)"

per the FSM

What's the low side reading when the compressor runs? Does it run at first, then cut off?
Reply With Quote
  #4  
Old June 20th, 2009, 21:28
lawsoncl lawsoncl is offline
NAXJA Forum User
 
Join Date: Jan 2006
Location: North Idaho
Posts: 5,611
Re: High pressure cutout switch not working?

Hmm. My 97 FSM says 500-600 psi on the high pressure cutoff, returning to normal at 400 psi. High side pressure depends on the ambient temperature, 300 psi is normal if its 90-100*F out. If its not that hot out, the FSM says check the condenser for airflow blockage or the system is overfilled.
Reply With Quote
  #5  
Old June 20th, 2009, 22:34
Saudade's Avatar
Saudade Saudade is offline
NAXJA Member
 
Join Date: May 2005
Location: SoCal
Posts: 2,427
Re: High pressure cutout switch not working?

Quote:
Originally Posted by lawsoncl View Post
Hmm. My 97 FSM says 500-600 psi on the high pressure cutoff, returning to normal at 400 psi. High side pressure depends on the ambient temperature, 300 psi is normal if its 90-100*F out. If its not that hot out, the FSM says check the condenser for airflow blockage or the system is overfilled.
That would be the relief valve on the compressor. The cut-off is the section before it.
Reply With Quote
  #6  
Old June 20th, 2009, 23:02
lawsoncl lawsoncl is offline
NAXJA Forum User
 
Join Date: Jan 2006
Location: North Idaho
Posts: 5,611
Re: High pressure cutout switch not working?

Whoops. You're right. I was thinking 450 was right, but wasn't paying enough attention when I looked.
Reply With Quote
  #7  
Old June 20th, 2009, 23:19
Saudade's Avatar
Saudade Saudade is offline
NAXJA Member
 
Join Date: May 2005
Location: SoCal
Posts: 2,427
Re: High pressure cutout switch not working?

Quote:
Originally Posted by lawsoncl View Post
Whoops. You're right. I was thinking 450 was right, but wasn't paying enough attention when I looked.
Point is the rest of your previous post was right on. 300 PSI is not excessive, at least not enough for the cut-off.
Reply With Quote
  #8  
Old June 20th, 2009, 23:46
chpmnsws6 chpmnsws6 is offline
NAXJA Forum User
 
Join Date: Jan 2009
Location: Springfield IL
Posts: 819
Re: High pressure cutout switch not working?

25-30psi on the low side. It staggers at 300psi (like the pump cannot push anymore)
Reply With Quote
  #9  
Old June 20th, 2009, 23:48
chpmnsws6 chpmnsws6 is offline
NAXJA Forum User
 
Join Date: Jan 2009
Location: Springfield IL
Posts: 819
Re: High pressure cutout switch not working?

Quote:
Originally Posted by Saudade View Post
"The high pressure cut-off switch contacts are open when the discharge line pressure rises above 3100 to 3375 kPa (450 to 490 psi). The switch contacts will close when the discharge line pressure drops to 1860 to 2275 kPa (270 to 330 psi)"

per the FSM

What's the low side reading when the compressor runs? Does it run at first, then cut off?

Sometimes it will blow cold for a half hour or so, then will die out.
Reply With Quote
  #10  
Old June 21st, 2009, 05:42
lawsoncl lawsoncl is offline
NAXJA Forum User
 
Join Date: Jan 2006
Location: North Idaho
Posts: 5,611
Re: High pressure cutout switch not working?

Quote:
Originally Posted by chpmnsws6 View Post
Sometimes it will blow cold for a half hour or so, then will die out.
Inside evaporator freezing up? I vaguely recall that being an issue on some years?
Reply With Quote
  #11  
Old June 21st, 2009, 06:48
winterbeater's Avatar
winterbeater winterbeater is offline
NAXJA Forum User
 
Join Date: Jul 2008
Location: Royal Oak, Michigan
Posts: 5,315
Re: High pressure cutout switch not working?

If your evap is freezing up, the airflow though the vents will be reduced. THe inlet line under the hood will still be frosty.
Reply With Quote
  #12  
Old June 21st, 2009, 23:11
chpmnsws6 chpmnsws6 is offline
NAXJA Forum User
 
Join Date: Jan 2009
Location: Springfield IL
Posts: 819
Re: High pressure cutout switch not working?

How do you test it? Check duct temps and see how cold they are getting before it heats up?

How many ounces of R134 does the system take (2001)?
Reply With Quote
  #13  
Old June 22nd, 2009, 13:40
chpmnsws6 chpmnsws6 is offline
NAXJA Forum User
 
Join Date: Jan 2009
Location: Springfield IL
Posts: 819
Re: High pressure cutout switch not working?

Bypassed the low pressure switch. It idles up but the compressor does not kick on. Next step?
Reply With Quote
  #14  
Old June 22nd, 2009, 13:42
chpmnsws6 chpmnsws6 is offline
NAXJA Forum User
 
Join Date: Jan 2009
Location: Springfield IL
Posts: 819
Re: High pressure cutout switch not working?

Also purged it some to see if 134 will come out. Its nothing but air coming out
Reply With Quote
  #15  
Old June 22nd, 2009, 17:39
winterbeater's Avatar
winterbeater winterbeater is offline
NAXJA Forum User
 
Join Date: Jul 2008
Location: Royal Oak, Michigan
Posts: 5,315
Re: High pressure cutout switch not working?

Evacuate and refill. Holds 1.25lbs (at least in a 2000).
Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Procedure for changing high pressure switch? (A/C) HMGanja OEM Tech Discussion 9 May 14th, 2009 20:11
OBA pressure switch not working? ZJeepX SoCal Chapter 0 February 5th, 2009 00:13
Air compressor pressure switch not working. ZJeepX Tow Rigs and Trailers 2 February 1st, 2009 17:23
Pressure switch that closes once a minimum pressure is reached?? twisted_ed Modified Tech Discussion 6 November 28th, 2006 11:14
oil pressure guage not working ctjeepman OEM Tech Discussion 3 September 25th, 2004 21:22


All times are GMT -7. The time now is 15:46.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2021, vBulletin Solutions, Inc.
NAXJA and NAXJA logo's Copyright NAXJA. All content/images Copyright NAXJA 1999-2014